Can you introduce calculation of the interstorey drift sensitivity coefficient θ in new buids of Tower 6?
EC8:
θ = Ptot/Vtot * dr/h * q ≤ 0,10
Ptot is the total gravity load at and above the storey considered in the seismic design situation
Vtot is the total seismic storey shear
dr is the design interstorey drift, evaluated as the difference of the average lateral displacements ds at the top and bottom of the storey under consideration, determined by a linear analysis based on the design response spectrum
h is the interstorey height.
BDS NPSSZR-2007:
θ = Ptot/Vtot * dr/h * 1/R ≤ 0,10
q=1/R is the behavior factor